Hi guys.

I got myself a zstick and incontrol Ha pro about 6 months ago and set everything up with my boiler thermostat set and after messing with the software for a while I simply gave up.

Now I'm no novice to electronics and automation, I work as an automation engineer in oil and gas commissioning and upgrading systems.

The last few days I decided to get incontrol up and running again and see what I could do.
On checking the logs I could see the device woke every hour, if I use a scene to set the thermostat set point it wouldn't work every time. In fact it worked only once.

I gave up and downloaded Domaticz and when using this I could see the polling time still set to 3600 seconds even though I'd changed it in incontrol.

With domaticz I was able to teach it the polling time and it stuck.

Returning to incontrol the device wasn't polling....
Changing settings to poll every minute in incontrol with a 5 minute polling on the device fixed this, as both seemed to be out of sync before.

Once I'd done this I get my level updates, can set the set point via a scene etc

It just seems that no matter how you try through incontrol the polling frequency didn't stick.

In fact the parameters didn't stick either.

The thermostat is a secure 318 which is the same as the horstmann thermostat hrt4 zw.

Cheers